Any refrigeration compressor with a shaft seal will leak. Period.
ALL shaft seals leak...It is by design...it is just a controlled leak with the final seal being a film of oil on the carbon ring/polished steel surface.
Under a vacuum....it will pull air in. So unless you have service valves on the compressor and can isolate it from the rest of the system your arguments do not hold water..( no pun intended )
Inches of vacuum is not the gold standard for leak testing.
Why ? because unless you are using a micron gauge you WILL have a rise in microns on a shaft seal and never see it on a vacuum/low side gauge.
1 inch hg vacuum = 25,000 microns.
Takes a lot of rise in microns before that needle on a gauge even thinks about moving...
Now...if the system is a completely HERMETIC system... yes, vacuum can be used as a method of leak testing...in fact I have pulled 50 micron vacuums on entire grocery store rack systems and held them for three days at 50 microns with the vacuum pumps turned off and disconnected from the system.
50 microns.....72 hours.....That my friends,,,is a tight system.
Nitrogen and R-22 Trace is the best way to leak test a system.
Oh,, and 350 lbs of pressure ??? you are really testing the bursting limits of the evap coil.... I have seen the float balls in compressor oil floats and coils inside of heat exchangers crush internally under those pressures.
150 psi is all you ever need..
think about it this way...say the internal surface area of an evap coil is 100 square inches....at 350 lbs per square inch...that's 35,000 pounds of force stored up in that little coil...just food for thought...