Yep, judging by the model number its probably a 4KW. Most of them are rated at intermittent duty or surge at that level.
Continuous duty is probably about 3.5KW.
Rule of thumb, figure volts times amps to get watts, 1,000 watts to the KW.
Motor starting is different. A motor, like a freezer, refrigerator or air conditoner can pull over 3 times the load when it is starting.
If you can find a information plate on the unit, look for two numbers.
FLA, is the Full Load Amps that the unit draws when running. Multiply that times the voltage, add a small fudge factor, and you have the wattage needed to run that unit.
LRA, is Locked Rotor Amps, which it the current it draws when starting. You genset has to be able to put out the much for a few seconds to get the motor started.
Don't forget that well filled deep freezes will stay frozen for quite a while unopened. So you can rotate plugging them in for a while each to keep more frozen than the genset can run all at one time.
As for the Briggs, the model number on them is quite a font of information. They put just about every aspect of that unit in their number.
Type of mount, type of carb, tank, everything. The code for it should be on their site.
I have two big motors on a couple of my pull behind bush hog mowers, and had the same problem with the oil drain.
Drilling a hole was not an option for me, due to the way the mower was made. Since that hole is a standard pipe thread, 1/4 or 3/8 inch, if I remember, I just put a 6 inch pipe extension with a valve on the end.
Because it would be going through brush, I got a valve with both ends threaded and screwed the plug in the outlet.
So, if a limb turned the little flag lever and opened the valve, I would not lose oil.
Also, made sure to tighten all the fittings really tight so they would not vibrate loose.