Can I hook up Lincoln ARC welder to my dryer outlet or do I need to have an electrician set me up somethin?
It will work as long as the welder does not pull more amps than the circut can handle. Most drier outlets are 30 amp. If your welder pulls more amps than that, dont do it.
Check the circut breaker or fuse for the drier and see what amperage it is rated for. Dont go over that rating.

Yeah, its the lincoln "buzzbox" 220 50AMP. I want to run a 25' cord from where the dryer outlet is to the garage. The dryer outlet is not used and has two 30 AMP breakers. Can I replace the 30 AMP breakers with 50 AMP ones and change the 4 prong dryer plug to a 3 prong parallel?
Just kidding. Please be careful.
Yeah, its the lincoln "buzzbox" 220 50AMP. I want to run a 25' cord from where the dryer outlet is to the garage. The dryer outlet is not used and has two 30 AMP breakers. Can I replace the 30 AMP breakers with 50 AMP ones and change the 4 prong dryer plug to a 3 prong parallel?
It depends on what kind of wire you run. If you use #8 THHN which is run in EMT conduit it will be fine.I am going to use a NEMA type 6-50 recepatacle wired to a 50 amp double pole breaker at the existing main breaker. Should I use #8 or #6 wire. The length will be about 30 feet.